I have a question about the use of ceiling fans in conjunction with upper room UVGI. I am aware of the effectiveness of air mixing and would like to include mixing fans in our implementation stratedgy for UVGI. We will be installing fixtures in both IPDs and ambulatory locations. I would prefer a ceiling fans to wall or floor mixing fans for the sake of easier administrative control and comfort. However, I am also aware that most commercially available ceiling fans rotate too quickly for this use. Importing from outside the country is not an option and our selection of commercially available ceiling fans is limited. We do not use mechanical ventilation, out average ceiling heights are 2.8-3meters and we will be installing upper room UVGI at a height of 2.13m
So:
How slow is slow? Is there a specific speed at which the fan needs to rotate in order to mix the air but not reduce the effectiveness of the UVGI? Can commercial fans be used? Is a fan rotating too fast better than no fan at all?
Unfortunately, I need to prepare a budget on this by the end of Oct 7, 2011….so quick replys would be greatly appreciated :)
Susan Adolph
ICO Uzbekistan/Tajikstan
MSF
Keywords: Engineering Controls

Grigory Volchenkov, MD
Dear Susan,
expand commentI don't think that higher fan speed reduces upper room UVGI fixture effectiveness. Actually more air mixing is better, the limiting factor for too quick fan rotation may be occupants comfort, not air decontamination efficiency. Theoretically ceiling fans should be more efficient in this regard than wall mounted or floor fans, because they provide more vertical air mixing than horizontal. In our study the floor standing fan improved upper room UVGI air decontamination efficiency for 16% (we have not tested ceiling fan).
Hard to say "how slow is slow". I think very low vertical air velocity of 0,25 m/s, which is considered only slightly sensible, still provides sufficient air mixing in the room. Ceiling fans usually provide much higher velocities (which is good for upper room UVGI). In low humidity settings (like Central Asia) at T 26C occupants prefer for comfort 0,4 m/s, at T 32C - 1,8 m/s.
Administratively and practically ceiling fans are easier to use in high risk settings (not in laboratory procedures rooms, since they can disrupt local ventilation and BSC function).
Needless to say how important to educate staff and patients that these fans reduce TB transmission ...
3:57 AM, 6 Oct 2011 | Permalink
S. Mehtar
Dear All
I not sure I totally agree with a fan to improve UVGI. There is centrifugal force of air movement which is not well controlled and the dispersal rates increase dramatically. Trying to get a fan and a UVGI should be in well controlled circumstances rather than an open room where air can escape. I think we need to be reminded that air has to move across the UVGI at a particular rate and that the mixing is to ensure that all the air circulates past the light. I am not sure that a ceiling fan can manage that.
I would love to hear from others
Regards
Shaheen
Prof Shaheen Mehtar
MBBS, FRC Path (UK), FCPath (Micro) (SA), MD (Lon)
Chair of Infection Prevention and Control Africa Network (IPCAN)
Head of Academic Unit for Infection Prevention and Control
Tygerberg Hospital &Fac of Health Sciences, Stellenbosch Uni
PO Box 19063,
Tygerberg 7505, Cape Town
Tel: +27 21 938 5051
Fax: + 27 21 938 5065
Mobile: +27 82 852 3697
http://www.sun.ac.za/uipc
Register now for the 3rd IPCAN conference Namibia
1-3rd November, 2011
http://www.ipcan.co.za
4:20 AM, 6 Oct 2011 | Permalink
paul bushnell
A little more info is required here first. What is the size of the room? What type of uvgi device are you using and what is their output? How many? placed where?
regards.
Paul.
4:36 AM, 6 Oct 2011 | Permalink
Edward Nardell, MD
I agree entirely with Grigory. There are study after study in experimental chambers showing that paddle fans always increase the effectiveness of upper room UVGI compared to natural vertical air mixing. One study by Riley and Permutt from 1972 did show that temperature generated air mixing, that is, delivering warm air low in the room which then rises, was even more effective than fans, but that requires a ventilation system and depends on the season (ie, delivering cool air to the upper room in summer to allow mixing), so is not practical. In Shelly Miller's more recent room studies using mixing fans (she used floor fans) were also effective, but were high velocity and therefor noisy and drafty. Our own studies in South Africa showing 80% efficacy used commercial ceiling fans run at slow speed. The speed considerations that Grigory explained are exactly correct - comfort being the main criteria. For reversible fans, most occupants prefer a downdraft during hot weather and an a less perceptible updraft during warm weather. Generally, the more mixing the better, within what is comfortable for occupants. Obviously, most ceiling fans are specifically designed for occupant comfort so this should not be a problem. We ...
expand comment7:58 AM, 6 Oct 2011 | Permalink
Susan Adolph
Thanks for the comments. I was concerned that a commercial fan, even at a slow speed, would be moving air through the irradiance zone too quickly to be effectively bactericidal. We are implementing this in 3 large inpatient facilities and approx 50 ambulatory treatment points, and xray rooms. It's quite a large financial commitment but our options for IC during a severe winters is limited. Thanks again for the advice.
Susan Adolph
ICO Uzbekistan/Tajikistan
MSF
10:56 PM, 6 Oct 2011 | Permalink
Edward Nardell, MD
To reiterate, more rapid vertical air mixing does not much affect efficacy because at faster rates droplet nuclei return to the upper room more often and exposure time is similar.
We could take this off line, but I would like to ask you publicly for the benefit of others what brand, style, and wattage UV fixtures you are using, and if you have a qualified consultant to: 1) plan the installation?, 2) commission it (meter for safety and efficacy) before you turn it on?, and 3) have a plan for long term maintenance including cleaning and re-lamping? Grigory Volchenkov has found that you can save a lot of money by not re-lamping on a annual basis, but metering each lamp in a standardized way and replacing those lamps which fall below, I believe, 60% of expected output. Like fluorescent lamps, UV lamps have mercury in them and should not end up in a landfill. You need a plan for safe disposal of all fluorescent lamps, including used UV lamps.
Ed
11:16 PM, 6 Oct 2011 | Permalink
Esther Buregyeya
Dear All,
Does anyone the author of the TB infection baseline tool found on ghdoline? www.ghdonline tbic-baseline-assessment tool version 10 April 8. If you know it kindly send me the name, as I need it for referencing purposes.
Esther Buregyeya
12:18 AM, 7 Oct 2011 | Permalink
paul bushnell
Hi Susan,with respect to all, the higher the fan speed, the less likely the efficacy of any upper air device (above a certain baseline). Work out the distance between the placement of the devices, then determine the average irradiance of said emitters/ devices in that area, you should be able to get the figure from the suppliers polar graphs, determine from that the amount of time the bugs need to be in that space " kill zone" , and then you can tell if your design is effective by using an anenometer measuring the air flow in the intended kill zones. If the irradiance is too weak, and / or fan speed to high, you run the risk of re activation if bugs are not killed properly on first pass. This is one of the problems with upper air device installations. Regards, Paul. You can e mal me at if you like.
3:05 AM, 7 Oct 2011 | Permalink
Mohamed Brahim Elkory
Bonjour,
Dans notre LNRM, on utilise pas Les ventilateurs de plafond mais plutôt le travail à travers des ESB.
Salutations.
------------------------------------------------------
Dr Mohamed Brahim Elkory
Directeur INRSP
Responsable du LNRM
BP : 695
Tél.:+222 45 25 31 34
Fax: +222 45 29 26 45
e-mail:
Nouakchott - Mauritanie
4:29 AM, 7 Oct 2011 | Permalink
Susan Adolph
Hi Ed,
expand commentI am happy to answer your questions publicly, please bear in mind they do not necessarily reflect the opinions of my organization. Do we have a qualified consultant? This is a resource limited setting in which has no experience with upper room UVGI. So there are no consultants from within the country. Personally, most of what I know about UV was taught to me by you and Grigory at the last Harvard course and I also have the support of a biomedical engineer via phone and internet. Our fixtures are a copy of a design of a well known commercial company who was willing to let us copy them. With these designs we are working together with a local manufacturer to produce them in quantity. This is a solution to importation problems, and also provides some sustainable access to these fixtures for a future when our organization is no longer here supporting the local MoH. They use a 30w lamp (imported Philips TUV-30). As for maintenance, this is a complicated issue. It will not be possible to measure all these lamps on a regular basis due their wide spread geographical distribution and limited transportation capacity and manpower on ...
5:13 AM, 7 Oct 2011 | Permalink
Sabine Verkuijl
Hi Esther,
The tool was developed by ICAP (International Centre for AIDS Care and Treatment Programs), South Africa in 2008.
Regards,
Sabine
8:01 AM, 7 Oct 2011 | Permalink
Edward Nardell, MD
With all due respect, Paul, you are wrong as explained previously and as shown in many room experiments. Please provide any evidence that a higher mixing rate will reduce killing. I can and will provide many papers that prove just the opposite. It is quite different in a duct where there is flow-through and only one chance to kill the bug. There you do have to use the Westinghouse tables that tell you how much irradiance you need for a given flow rate, but for upper room UVGI, that is not the case, either in theory, or by experiment. The faster the mixing the more opportunities the bugs have to reach the upper irradiated zone. I will send the citations along from my office computer.
Ed
8:18 AM, 7 Oct 2011 | Permalink
Hans Mulder
Just a practical tip from my side, there are single or two directional ceiling fans, they either create and down ward or can create an upward and downward flow of air. This will probably not affect the mixing of the air, but will have a great impact on patients. In winter a downward flow over the bed might feel very uncomfortable, especially when facility is not heated properly. In summer a downward flow over the bed might be a good thing. If possible get the two directional ceiling fans, and switch directions twice a year.
Regarding the "home" made lamps. I only can say have them tested. The use of cheaper materials to fabricate the lamps might be of a disadvantage later, bent reflectors, low(er) efficiency or difficult to maintain.
One other point I want to make. Is there money available to run the equipment? From my own experience I have often heard that UVGI/ventilation is not switched on because there is no money for electricity. In some cases this might be true, in others not, but it might happen that expensive installation are not used for this reason. \
Hans Mulder
11:58 AM, 7 Oct 2011 | Permalink
S. Mehtar
Sorry, but I do agree with Paul, hence my first response but I bow to those with much greater knowledge than mine.
S
Prof Shaheen Mehtar
MBBS, FRC Path (UK), FCPath (Micro) (SA), MD (Lon)
Head of Academic Unit for Infection Prevention and Control
Tygerberg Hospital &Fac of Health Sciences, Stellenbosch Uni
PO Box 19063,
Tygerberg 7505, Cape Town
Tel: +27 21 938 5051
Fax: + 27 21 938 5065
Mobile: +27 82 852 3697
http://www.sun.ac.za/uipc
Visit the IPCAN website on
http://www.ipcan.co.za
12:11 PM, 7 Oct 2011 | Permalink
Sophie Beauvais
Dear All,
Just a quick translation: Answering to Ed Nardell's question (For the benefit of others what brand, style, and wattage UV fixtures you are using, and if you have a qualified consultant to: 1) plan the installation?, 2) commission it (meter for safety and efficacy) before you turn it on?, and 3) have a plan for long term maintenance including cleaning and re-lamping?), Dr Mohamed Brahim Elkory at the National Lab in Mauritania wrote earlier that they do not use the ceiling fans and instead do the lab work in a bio safety cabinet.
1:39 PM, 7 Oct 2011 | Permalink
Edward Nardell, MD
For clarity, in response to Mohamed, this discussion was not about lab use of upper room UV or paddle fans in the lab setting. Usually, fans are not used in labs where concentrated cultures are being opened for fear of dissemination or contamination, and also because they may well interfere with the proper function of a biological safety cabinet. The use of upper room UV and fans is generally in clinical and other congregate settings.
Ed
2:18 PM, 7 Oct 2011 | Permalink
Edward Nardell, MD
I just added a document to GHDonline labelled as Riley 1971. It is two papers from the Archives of Environmental Health Here is my summary:
Download: Riley_1971_-_Arch_Environ_Health_22-1.pdf<http://www.ghdonline.org/uploads/Riley_1971_-_Arch_Environ_Health_22-1.pdf> (1.4 MB)
Summary: These two articles from the older literature show in great detail, based on room experiments, that air mixing greatly enhances the efficacy of upper room UVGI. In the first article the authors show that convection currents caused by temperature differences in the room were the most effective way to mix air - when this could be accomplished by mechanical ventilation. This is not feasible in most places in poor settings where UV is used. For most applications, ceiling fans are better. The second paper shows that air mixing doubled the effect of UVGI. Although more rapid air movement through the upper room means less exposure time per pass, it also means more passes through the upper room. There are several more papers in the literature confirming that there is no "down side" to improved air mixing when using upper room UVGI and probably no optimal fan speed, except for comfort of occupants.
To access the articles please log into GHDonline TB IC ...
3:05 PM, 7 Oct 2011 | Permalink
Susan Adolph
Again, thank you all for your comments, they've been very helpful.
Susan Adolph
2:36 AM, 8 Oct 2011 | Permalink
Mohamed Brahim Elkory
Bonjour,
Je vous remercie pour l'info.
8:01 AM, 8 Oct 2011 | Permalink
Robert Spiteri
Good Day
expand commentMy name is Rob.
I have had nothing to add to other conversations, but this one I can
contribute to.
Ceiling Fans come in various shapes and sizes. Some with fancy lights and
two fan settings.
Industrial type with three settings - fast, medium and slow
The above are not suitable for UVGI work.
The heavy duty industrial type have five settings. These are suitable.
My experience of pedal fans, I use them where possible but you must be aware
of some of the down sides.
If the pedal fan is placed too close to the UVGI unit, in my opinion and my
tests, the unit efficiency will be reduced.
On the other hand, if the unit is placed far from the UVGI unit, the
efficiency is increased, reducing the number of pathogens in the air.
Further downsides - this is from the African scenario
Tin roof with extremely thin ceiling board: Temperatures between 25 and 30
degrees C.
Placing a pedal fan in this situation creates extreme discomfort to the
patients, as this makes the air extremely warm.
In winter or early morning when its +5 degrees C the use of a pedal fan
makes it extremely cold and ...
10:19 AM, 8 Oct 2011 | Permalink
Edward Nardell, MD
Dear Rob,
expand commentThanks for your contribution, but you are mixing apples and oranges.
Let's first talk about UV air mixing systems, and then ventilation. You are mixing them up.
First, how do you know that putting a ceiling paddle fan close to a UVGI fixture decreases efficiency? How do you know that putting it further away increases efficiency? These "opinions" need to be backed up with evidence to be useful and that kind of evidence is very hard to generate. Until recently there have only been experimental room studies with aerosolized bacteria and microbiological air sampling. I have just posted two such studies. Now there are to real hospital studies using guinea pig air sampling. That by Escombe has been published and the pdf is on GHDonline. Our similar study is being prepared for publication. The sum total of the experimental data does not support what you say. Air mixing is important for upper room UVGI efficacy no matter how you do it. Occupant comfort in achieving air mixing is important, otherwise fans will be turned off. Hence, slow moving paddle fans - in one direction or the other depending on the season and temperature considerations - is the mixing method ...
10:47 AM, 8 Oct 2011 | Permalink
Dries Meyer
I am replying at a late stage due to some serious Lion photography in an area where the worst polluted air smell was that of fresh Elephant dung and of course no TB infected Buffalo.
expand commentThe basic operation principal of Upper volume UVGI is to use a low UV-C irradiation level to irradiate a large volume of slow moving air.
UVGI must "touch" the surface area of the TB bacteria for a certain time to deactivate it. The UVGI irradiation dose is expressed as µW/cm². In older literature the Pennsylvania State University found that a dose of 10µW/cm² is effective for the deactivation of TB bacteria. When airflow or air movement is involved, the deactivation unit generally accepted and used in air conditioning systems is 10 000µWseconds/cm².
A very important factor to remember is that in a closed volume with high air movement, the TB bacteria will be "weakened" every time it passes through the irradiated area until it is deactivated. I prefer to use the term air movement because the air in the room is moved and not changed.
The important part of any UVGI design is that the irradiation dose must not be lower than ...
6:04 AM, 10 Oct 2011 | Permalink
Edward Nardell, MD
Dear Dries,
expand commentAs moderator, I need to interject a couple of points. First, there is now a fair amount of repetition on this topic and we are risk of continuing this thread too long. Not everyone on GHDonline wants to continue to read about fan speed. Second, as a group we are better served by data than by opinion, so please try to substantiate what you write with data. Thirdly, I need to correct a few points, below.
The effective UV dose is expressed as the "Z value" which is the decrease in natural log of the kill ratio of numbers of colonies divided by the UV dose. See the ratio below, if the slide transmits, or in words it is the natural log of the kill rate for a certain microbial species divided by the UV dose. To be relevant to upper room UVGI, that measurement must be taken in air where nearly naked infectious droplet nuclei are extremely vulnerable, not on surfaces, where organisms can clump together or be covered by a fluid layer. There have been many studies of Z for TB using laboratory and clinical strains and they are similar as shown in the slide below ...
9:29 AM, 10 Oct 2011 | Permalink
Dries Meyer
Dear Ed,
Thanks for the reply.
When will the Witbank report be published. We need the results urgently in the RSA and I am sure it will be of help in most other countries.
Regards,
Dries Meyer.
11:39 AM, 10 Oct 2011 | Permalink
Edward Nardell, MD
I am adding a slide presentation on upper room UVGI, given to the Am Soc of Photobiology. The 13th slide is about the Z value, that is, the susceptibility of microorganisms to UVGI.
Attached resource:
Source: Brigham and Women's Hospital, Division of Global Health Equity
Keywords: Engineering Controls
8:31 PM, 10 Oct 2011 | Permalink
Susan Adolph
Hello All,
I now have a related question, let me know if I should post it as a separate discussion.
As I mentioned earlier, we will be installing approximately 600 upper UVGI fixtures (3 TB inpatient hospitals, and about 30 ambulatory TB treatment locations). It may not be feasible to install the same amount of ceiling/paddle fans. So, if I need to prioritize which locations receive fans, I need to develop some sort of criteria. My thoughts so far are to use infectiousness, followed by resistance pattern. For example, highest priority to diagnostic locations (TB doctors’ offices, xray etc) followed by resistance, XDR, MDR, PDR etc. However, in many of our ambulatory locations there is no segregation by resistance, and although the patients there are all on treatment, this treatment is sometimes initiated in these ambulatory locations and therefore we have a lot of mixing between infectious and non infectious patients with various resistance patterns (segregation by scheduling patients to come at certain times of the day is also not possible). Any thoughts on how to prioritize which locations receive a fan?
Susan Adolph,
ICO Uzbekistan/Tajikistan
MSF
10:52 PM, 10 Oct 2011 | Permalink
Edward Nardell, MD
Susan, please re-post as "Priorities for UVGI use in high-burden settings" I am concerned that many readers will not even open yet another posts on fans, per se.
Ed
11:23 PM, 10 Oct 2011 | Permalink
paul bushnell
Susan do you have an e mail address that you can be contacted on. rgds. Paul.
1:27 AM, 11 Oct 2011 | Permalink
Francoise NYWAGI LOUIS
Dear all,
Can I suggest that we have a wrap up on this very relevant discussion (Ed? Paul? some one else?), as the multiplication of messages makes the whole topic finally very confusing....because of pros and cons etc...
I would suggest that someone summarizes the topic for us
Thanks a lot for this
Have a great day
Francoise
2:59 AM, 11 Oct 2011 | Permalink
Paul A. Jensen, PhD, PE, CIH
Great suggestion . . . We can have a summary position drafted regarding this string of discussion, allow a short time for comment, and then deal with additional topics. And, we would request follow discussions as Susan and others implement UVGI.
Regards,
Paul J
--------------------------
Sent from my BlackBerry . . . Please excuse my fumbling thumbs!
3:16 AM, 11 Oct 2011 | Permalink
Philippe Creach
Dear All,
Before giving consideration to any engineering measures and discussing their (relative) efficacy at length in details not always understandable, I would imagine that ensuring proper separation of patients is the must and funds should be dedicated to it at the first place. UVGI appears somehow as damage control in the context of Uzbekistan/Tajikistan and I am very doubtful on their real efficacy in these contexts.
Best wishes,
Philippe Creac'h
5:14 AM, 11 Oct 2011 | Permalink
Marina Shulgina
Dear Edward,
I could not find the presentation you mentioned in the message below. How
can I get it?
10:01 AM, 11 Oct 2011 | Permalink
Edward Nardell, MD
You click on the link to GHDonline and will see the attachment there to this discussion and you click on it there. I have asked the administrator of GHDonline to repost the document as a PDF to protect it from being changed. One hates to see slides show up elsewhere modified to make some other point, or out of context. It could be in transition. Wait a day or two before looking for it and it should be there. The slide that I was referring to is actually slide #14, not 13.
Ed
Edward A. Nardell, MD
Associate Professor
Harvard Medical School (Medicine; Global Health and Social Medicine)
Harvard School of Public Health (Environmental Health; Immunology and Infectious Diseases)
Brigham and Women's Hospital
Division of Global Health Equity
FXB Building, 709c
651 Huntington Ave.
Boston, MA 02115
617 432-6937 617 877-9412 (Cell)
(preferred) or
10:15 AM, 11 Oct 2011 | Permalink
Marina Shulgina
Thank you very much
12:13 PM, 12 Oct 2011 | Permalink