Engineering control

Started by amal salah eldin on 01 Nov 2011
Last edited by Sophie Beauvais on 11 Jan 2012

HI All
Please i want to ask , is there a standard codes for the sizes of windows and doors of MDR-TB isolation rooms . Taking in consideration we depend on Natural ventilation , also portable HEPA filters and upper UV lamps .

Keywords: Engineering Controls 

Replies (36) Add reply
1

Tariq Alexander Qaiser

Window sizes and locations need to be established based upon environmental conditions at YOUR location. Select window locations that provide cross ventilation and a maximum of air changes and air dilution. Most importantly windows need to be kept OPEN.

I don't know of any portable HEPA filter units that work for the volume of a room.

6:51 PM, 1 Nov 2011 | Permalink

2

Paul A. Jensen, PhD, PE, CIH

Greetings!

In addition to Tariq's comments, I'd like to add that some folks use a rule-of-thumb that the openings (on opposite sides of the room) should be at least 10% of the square of the room. There are other rules of thumb based on the length vs. height of the room. There are also ways to optimize based on local climate. So, there are some design issues that could possible take up pages!!! On source for info is the WHO 2009 Natural Ventilation Guide for Healthcare Settings (That may not be the proper name; however, it's close!). I will send the link tomorrow.

As far as room air cleaners (RACs) go, one must either get the Clean Air Delivery Rate (CADR) from the manufacturer or determine it experimentally. Many room air cleaners have a very low CADR . . . Hence, you may need MANY in order to get 6-12 ACH!!! Also, because the inlet and outlet of RACs are usually relatively close to each other and generally not designed for good air mixing in a room, their actual efficiency may be lower that the calculated ACH (based on the CADR). RACs are NOT needed if you have well-designed natural ...

expand comment

8:14 PM, 1 Nov 2011 | Permalink

3

Robert Spiteri

Good Morning
could i ask you to send me the link as I've not seen this info WHO 2009
Natural Ventilation Guide
Thanks

Kind Regards,

Robert Spiteri
Ozone Purification Technology
Aerobiological Tech-Eng
Cell: 082 400 9291
Tell: 011 462 5525
Fax: 086 607 6638
www.uvozone.co.za

3:15 AM, 2 Nov 2011 | Permalink

4

Dries Meyer

Amal Salah Elden.

The volume of the room plays an important part in the air flow rate and
window opening size.

The bigger the volume, the bigger opening windows are required.

The tendency with natural ventilation designers are to create large
wards with large volumes by not using ceilings and using higher walls
than normal. This means that a higher natural air flow rate is required
to obtain the required ACH. The walls are raised to provide for
additional air movement to compliment that of the windows. The designs
are also mostly based on single loaded passages.

This type of design is not suitable for 99% of existing buildings and
all the new "experimental" natural ventilation ward designs available,
are based on single wards with toilet facilities. To build single ward
facilities in developing and under developed countries will simply be to
expensive.

To me it also raises the question that if a patient under treatment is
separately housed in a single ward with its own toilet facility, nursed
by HCW's and and other personnel wearing respirators, is this elaborate
design required ?

Will a single ward for this purpose, with a normal ceiling height and
cross ventilation by window ...

expand comment

3:24 AM, 2 Nov 2011 | Permalink

5

Tariq Alexander Qaiser

In my opinion the best option is in a single occupancy room with an independent toilet, serviceable from a single loaded corridor.
The room should have a low volume and open windows on opposite sides. Perhaps a window and louvered doors/ ventilator above the door. Fly screens are a must but will cut the air flow by a substantial amount. ( Some times over 50%)

3:39 AM, 2 Nov 2011 | Permalink

6

Paul A. Jensen, PhD, PE, CIH

"Natural ventilation for infection control in health-care settings" (WHO guideline 2009) may be found at the following link:

http://www.who.int/water_sanitation_health/publications/natural_ventilation/e...


 
Regards,
 
Paul J

8:15 AM, 2 Nov 2011 | Permalink

7

amal salah eldin

Thank you Tark & Paul for your support and valuable discussion

3:42 PM, 2 Nov 2011 | Permalink

8

Robert Spiteri

i would like to agree in the ideal world a single room per person.

Come to Africa where you could have 80 + in one room and the beds are so
close that you cannot walk between the beds,a window so small that it is no
bigger than that of a single
toilet and some strange exhaust arrangement to take air out of the building
that is so suspect.

Many Windows here in Africa havesSecurity bars and sealed closed for
security reasons

There is a place in Africa where the patients are HIV + MDRTB and this is
the environment they have been living in.

Have you ever sat in a room with 6ACH at night +15 Deg C- its not pleasant,
now with 12ACH you can not heat the room

Most Patients only have one blanket and sleep fully clothed in winter.


In the morning when its at its coldest between 4.30 - 6.30 am the chill
factor outside is +7 Deg C the patients huddle together to keep warm.

The cost of heating is not an issue in some places in the world, but in
Africa it is.

Here in Africa infection control is a word that can ...

expand comment

3:50 PM, 2 Nov 2011 | Permalink

9

Edward Nardell, MD

Just a few comments in response to Dries:

1) If patients are quickly diagnosed and placed on EFFECTIVE therapy (based on knowldege of drug resistance), infectivity drops very rapidly and separation need not be long, greatly reducing the demand on isolation rooms. Remember that in many parts of the world TB, even MDR TB, is treated entirely in the community. However, rapid, specific diagnosis of TB and drug resistance is not yet widely available through Gene Xpert, and other methods, so separation, and exposure reduction may be needed because patients may not be on EFFECTIVE therapy and may remain infectious. This is especially true for re-treatment cases and those who could have highly resistant TB, such as XDR-TB.

2) The challenges to engineering controls are very different in urban and rural settings, where space is often available to spread out. IF space is available, we have seen a number of inexpensive designs for single occupancy structures that use natural ventilation, but do not depend entirely on good directional air movement because physical separation is doing much of the job of preventing transmission. True, health care workers usually must enter the room and need to be protected. Natural ventilation combined with ...

expand comment

5:19 PM, 2 Nov 2011 | Permalink

10

S. Mehtar

Dear All, Sounds like Robert Spiteri has summarised the issues dealing with TB in African HCFs. I have just got back from a wonderfully exciting Infection Control Africa Network meeting in Namibia and we had all sorts of interesting topics including of course TB. There were some quite interesting solutions presented.
Thanks
S

Prof Shaheen Mehtar
MBBS, FRC Path (UK), FCPath (Micro) (SA), MD (Lon)
Head of Academic Unit for Infection Prevention and Control
Tygerberg Hospital &Fac of Health Sciences, Stellenbosch Uni
PO Box 19063,
Tygerberg 7505, Cape Town
Tel: +27 21 938 5051
Fax: + 27 21 938 5065
Mobile: +27 82 852 3697
http://www.sun.ac.za/uipc
Visit the IPCAN website on
http://www.ipcan.co.za

10:17 AM, 5 Nov 2011 | Permalink

11

S. Mehtar

I am sorry I was away and have just joined. I would like to reply to Tariq with some of the realities. Where one has a case or two of TB a month, or even a year, that is really no problem- we admit 7 to 15 new cases a day and at any one time have between 10 to 20 diagnosed cases of TB at TBH. The hospital was built a while back and like the hospitals in other parts of the world, do not have en-suite facilities and often in Africa, no assisted ventilation. It is a really interesting situation and the IPC practitioners must put all their skills, knowledge and experience to at least reduce if not eliminate transfer of TB- believe me it is not easy but is "do-able"- one needs are really dedicated team to make sure things happen.

Prof Shaheen Mehtar
MBBS, FRC Path (UK), FCPath (Micro) (SA), MD (Lon)
Head of Academic Unit for Infection Prevention and Control
Tygerberg Hospital &Fac of Health Sciences, Stellenbosch Uni
PO Box 19063,
Tygerberg 7505, Cape Town
Tel: +27 21 938 5051
Fax: + 27 21 938 5065
Mobile: +27 82 852 3697
http://www.sun.ac.za ...

expand comment

10:37 AM, 5 Nov 2011 | Permalink

12

S. Mehtar

IT IS A GOOD DOCUMENT.

Prof Shaheen Mehtar
MBBS, FRC Path (UK), FCPath (Micro) (SA), MD (Lon)
Head of Academic Unit for Infection Prevention and Control
Tygerberg Hospital &Fac of Health Sciences, Stellenbosch Uni
PO Box 19063,
Tygerberg 7505, Cape Town
Tel: +27 21 938 5051
Fax: + 27 21 938 5065
Mobile: +27 82 852 3697
http://www.sun.ac.za/uipc
Visit the IPCAN website on
http://www.ipcan.co.za

10:38 AM, 5 Nov 2011 | Permalink

13

Tariq Alexander Qaiser

Thanks Shaheen,
As an architect in Pakistan I really worry about the spaces being used to care for patients.
These discussions do speak the case for home based care. Home based care in poor crowded neighbourhoods also raises worry some questions.
There is also the question when a patient on treatment will stop passing on TB. ( Reference Dr ED Nardell)
The diseases are multiple, and the solutions need to be adaptive to local contexts.
However I do believe strongly that if we are searching for solutions then the Best practice / protocols need to be discussed first. Compromises are a fact of life. But we have to try for the best. And then for the possible.

11:36 AM, 5 Nov 2011 | Permalink

14

S. Mehtar

Dear Tariq
I am from Pakistan and have been working there although I was trained and lived in England until I came to South Africa. I know exactly what you mean and I think some of the problems are quite challenging. We deal with a lot of TB in South Africa and have managed a reasonable compromise. I don't think it might be possible in Pakistan since the bed occupancy is 150% and there are people lying all over the place. In Karachi it is possible to put the patients out along the veranda; at least there is some breeze and the temperature is tolerable; the last time I was there, that is what I suggested and it seemed to work (not very easy though) but is not possible in the Punjab, I'm afraid. In the camps it is even more of a problem. In the home, there is a different challenge but not that different from South Africa. My Unit has a teaching programme for patients and healthcare workers in the community and it seems to work quite well (on the face of it anyway) but we have not been able to analyse the cross infection- hopefully ...

expand comment

11:50 AM, 5 Nov 2011 | Permalink

15

Ejaz Qadeer

Dear All
Very interesting discussions we are planning to upgrade some hospitals for MDR which is not purpose built. I will appreciate if you could guide me in this regard please find attach a drawing of a MDR ward with our plan to upgrade for infection control.

11:59 AM, 5 Nov 2011 | Permalink

16

Moustapha NDIR

Dear all
I just come from a course on Tb infection control held in Mexico city.
Every field of IC was exposed and discussed, and health centers were
visited. I think that the intervention of Dr Paul jensen in this debate
brings enough light to us.
best regards

--
Dr M.NDIR
ConsultantTB, BP 25063 Dakar-Fann
Sénégal
cell:+221776368963

12:11 PM, 5 Nov 2011 | Permalink

17

Edward Nardell, MD

I would like to respond to several points raised by Rob Spiteri - one very genaral response on the importance of advocacy for change, and the other very specific on a citation he referred us to.

1) First, the conditions that Rob describes are truely horrific. One can speak of cost-effective interventions for poor settings but at some point you have to stop and say that conditions will not improve without the infusion of resources and that there are not good, workable solutions if resources cannot be found. Fortunately, conditions have improved in many impoverished places, but too few. Rob, I believe that advocacy for resources and change are the only solution for the conditions you describe.

2) two technical issues: disposable respirators can and should be re-used as long as they are structurally intact, ie, that a good face seal is possible. The elastic is the usual first thing to go, but molded respirators can also get crushed and loose their ability to seal.

Another technical issue is your point on UV and turbulence. You have many bigger issues in your note, but I did search out this paper and could obtain only the abstract thus far. From the abstract ...

expand comment

1:43 PM, 5 Nov 2011 | Permalink

18

Ejaz Qadeer

Dear Qaiser and Prof Shaheen
National TB Control Program is facing the challenge of implementing optimal infection control measures as part of National MDR Program. The problems are MDR wards are not purpose built ,overcrowded OPDs and limited natural ventilation of wards , climate ,untrained staff. I will appreciate if you could guide me in this regard particularly I am interested in teaching program which Prof Shaheen has mentioned.

2:03 PM, 6 Nov 2011 | Permalink

19

S. Mehtar

Dear Ejaz
We too, do not have purpose built isolation facilities to the extent to which I would like, but one has to do one's best. Shall we communicate outside this forum to see what we can do? I know there is a PMIS meeting in Karachi in Dec- is that a good forum for Pakistani specialists to discuss matters of urgency?
Regards
Shaheen

Prof Shaheen Mehtar
MBBS, FRC Path (UK), FCPath (Micro) (SA), MD (Lon)
Chair of Infection Control Africa Network (ICAN)
Head of Academic Unit for Infection Prevention and Control
Tygerberg Hospital &Fac of Health Sciences, Stellenbosch Uni
PO Box 19063,
Tygerberg 7505, Cape Town
Tel: +27 21 938 5051
Fax: + 27 21 938 5065
Mobile: +27 82 852 3697
http://www.sun.ac.za/uipc
Register now for the 3rd IPCAN conference Namibia
1-3rd November, 2011
http://www.ipcan.co.za

1:29 AM, 7 Nov 2011 | Permalink

20

Edward Nardell, MD

Pakistan is an interesting situation of high MDR case rates and limited resources, generally, but much recent input of creative approaches, local philanthropy, and global fund dollars. Tariq is the architect of a remarkable new MDR ambulatory facility and laboratory in Karachi designed after attending the 2-week summer course on airborne infection control. It employes the natural breeze and shaded outdoor waiting areas that are possible in Karachi because of the climate. Perhaps Tariq would post some of these photos. Much of the funding for the Indus Hospital in Karachi comes from private philanthropy, so not everyone can do what they did. In addition, indus is treating a large population in Karachi with ambulatory MDR treatment, monitored closely by cell-phone geotracking - with outside funding I believe. Like PIH's programs in Peru and Lesotho, and others in Cambodia, the Philippines, and Ethiopia, the Indus MDR program does not depend on in-patient treatment and does not have to deal with large numbers of individual isolation rooms. There is evidence that TB patients become rapidly non-infectious on effective therapy, so I believe this is the long-term solution to the isolation problem - don't - manage most MDR patients as out-patients - except XDR TB ...

expand comment

8:53 AM, 7 Nov 2011 | Permalink

21

Catherine Noakes

Just to clarify, the paper referred to about turbulence and UV is about UV installed in ventilation ducts rather than upper-room systems. Turbulence may be an important parameter for an in-duct system, simply because you only have one shot at disinfecting the air and therefore design of the unit has to be such to maximise kill at a particular flow rate. As an upper-room system relies on circulation of the contaminated air from the occupied zone through the UV zone, it is the mixing that is important. A well designed ventilation system can achieve a good level of mixing without intervention, however as indicated by Rob Spiteri this may change with season and the reality is that there are many poorly designed mechanical and natural ventilation systems out there. As Ed states paddle fans can be a simple and an effective method of enhancing the mixing in many environments. From a fluid dynamics perspective, all room air is turbulent, and for upper room UV this may even be beneficial as turbulence promotes mixing.

Best regards

Cath

------------------------------------------------
Dr Catherine Noakes CEng, MIMechE
Reader in Infection Control Engineering
Director of Pathogen Control Engineering Institute
School of Civil Engineering
University of Leeds
Leeds ...

expand comment

10:48 AM, 7 Nov 2011 | Permalink

22

Ejaz Qadeer

Thanks sure we can discuss while you are in Karachi,

11:18 AM, 7 Nov 2011 | Permalink

23

S. Mehtar

I am not coming I am afraid. But we shall keep in touch.
Regards
Shaheen

Prof Shaheen Mehtar
MBBS, FRC Path (UK), FCPath (Micro) (SA), MD (Lon)
Head of Academic Unit for Infection Prevention and Control
Tygerberg Hospital &Fac of Health Sciences, Stellenbosch Uni
PO Box 19063,
Tygerberg 7505, Cape Town
Tel: +27 21 938 5051
Fax: + 27 21 938 5065
Mobile: +27 82 852 3697
http://www.sun.ac.za/uipc
Visit the IPCAN website on
http://www.ipcan.co.za

12:19 PM, 7 Nov 2011 | Permalink

24

Shelly Batra, MD

Dear All,

Thank you for the insightful discussion. I fully agree with Ed. All
discussion of isolation for MDR-TB is futile in countries such as India,
where there is a huge TB burden, and the extent of burden for MDR and XDR
is not even known fully.

My organisation, Operation ASHA, is successfully carrying out treatment
of MDR TB patients in Delhi, India, and patients stay in their own homes
with their families. We are using the community DOTs centres to provide
directly observed therapy for MDR patients. Our biggest challenge has been
to ensure adherance for the 2 year long treatment, which we have overcome
by intensive and repeated counselling of patients and families, using CHWs,
who belong to the community they serve.Another challenge has been the
discrimination faced by MDR-TB patients. Family members and friends of
patients seem to believe that they will surely get infected! Once again,
education has helped greatly in de-stigmatising MDR-TB, and of course in
preventing spread. The sun and the wind have helped greatly, and weather in
India is such that we can effectively use the power of nature to dispel
/kill Mycobacteria.

Isolation is expensive, and maybe hospitals are providing it ...

expand comment

12:20 PM, 7 Nov 2011 | Permalink

25

Robert Spiteri

In response to UV installed in ventilation ducts, if UV is installed in an
HVAC system, the air velocity is generally constant. A well designed system
would be lamps that are placed through the middle of the air stream. This is
based on the knowledge of the lamp's behaviour knowing that the intensity of
the lamp will reduce by a certain percentage year by year. This ensures
longevity of the system.

Rob spiteri

1:52 PM, 7 Nov 2011 | Permalink

26

Dries Meyer

A very important factor left out in previous correspondence is Dwell
Time. That is the time required to deactivate a bacteria with a specific
UVGI dose, ie the term µWs/cm².

Induct air conditioning systems must be provided with an irradiation
chamber to ensure that the air remain in the chamber for sufficient time
to allow the UVGI to deactivate the bacteria in one pass. The dwell time
will take care of the deactivation whether there is turbulence or not.

This is also applicable to upper volume UVGI where the irradiated upper
volume is the "irradiation" chamber. In this case it may require that
the bacteria pas through the irradiated volume more than once to be
deactivated because of the low UVGI dose.

It may be the ideal place if the UV-C lamps are placed in the centre of
an air stream, but keeping in mind that this is the part of the "duct"
with the highest airflow because there is no friction, The number of
UV-C lamps required may affect the airflow in high velocity systems.
Every installation must therefore be designed to suit the specific
application.

Dries Meyer.

1:51 AM, 8 Nov 2011 | Permalink

27

Robert Spiteri

Thanks Dries.
The information that you would require to place UV in a duct:

- understanding the lamp, that only 1/3rd of the lamp's total wattage is UVC
- the tables that are available on the internet by Kolwasky hold good for
induct sanitation of Air Con
- if you want to go the long method, UV Exposure Dose (Fluence) Microbes
exposed to UV irradiation are subject to an exposure dose (Fluence) that is
a function of the irradiance multiplied by the exposure time, as follows:

D = Et • IR

where
D=UV exposure dose (fluence), J/m2
Et=exposure time, sec
IR= Irradiance, W/m2

Secondly, the tables must be found for the micro organisms you wish to
control. These tables are also found on the internet or in Kolwasky's books

Rob

12:07 PM, 8 Nov 2011 | Permalink

28

Edward Nardell, MD

I would like to cut off further discussion of UV in ducts as not entirely appropriate for this group. First, many of the readers are working in areas without mechanical ventilation systems. Secondly, it is of little comfort to know that only when the air leaves the room is it disinfected by the UV in the ductwork. What is usually needed is air disinfection in the room occupied by the infectious source and workers or other patients. For that we need upper room UVGI-air mixing systems. Air cleaning machines are also used, but most often do not move enough air to be very useful.

This detail on duct UV is probably not of great interest to our readership.

Ed Nardell, MD, moderator

1:25 PM, 8 Nov 2011 | Permalink

29

Robert Spiteri

How does one assess the UVGI fixture assuming a salesman has arrived at your
doorstep and offered you the equipment?

TYPE OF EQUIPMENT OFFERED

A
B
C

Round
Rectangular
Round

9W UVC Lamp
36W UVC Lamp
2 x 18W UVC Lamps
1 Fan facing downwards 123cm/H 1 Fan
downward facing with grill 37cm/H 2 Fans 80cm/H
facing outwards no grill
UV Fixture 5 Louvers
UV Fixture 5 Louvers
Optional - No Louvers


3, 5 or 9 Louvers
Mercury content set by Manufacturer Mercury
content set by Manufacturer Mercury content
set by Manufacturer
No additional features
Additional features - Titanium dioxide

Ionizer
Ease of maintenance - can only be carried Can be
maintained by medical engineering crew Can be maintained by
medical engineering crew
out by a fully skilled member of manufacturer
staff
No training given to hospital engineering staff No training
given to hospital engineering staff Training given to
hospital engineering staff
on maintenance
on maintenance
Installation as per National Institute of Electrical Installation
as per National Institute of Electrical Installation as per
National Institute of Electrical
Engineers
Engineers
Engineers/ Clinical & Hospital Engineers

All three comply to eye safety

Reliability:

Early lamp failure - Possible 5% Early
lamp failure - 1%
Early ...

expand comment

3:44 PM, 8 Nov 2011 | Permalink

30

Robert Spiteri

Sorry guys but the information did not come out in table form as intended. I
will resend once I understand what went wrong.

Rob

3:51 PM, 8 Nov 2011 | Permalink

31

Shelly Batra, MD

Though not applicable in resource limited settings, it is actually
interesting to read what others are doing, and great to know how
engineering has the potential to dispel/destroy Mycobacteria.

--
*Shelly Batra, MD
*
President*

*This email and any attachments to it may be confidential and are intended
solely for the use of the individual to whom they are addressed. Views or
opinions expressed therein do not necessarily represent those of Operation
ASHA. If you are not the intended recipient of this email, you must
neither take any action based upon its contents, nor copy or show it to
anyone. We apologize if you have received this email in error.*
*

1:46 AM, 9 Nov 2011 | Permalink

32

Dries Meyer

I agree with Ed that in duct UVGI should not form part of this
discussion and I want to add that participants should not copy parts of
handbooks directly or indirectly in the discussion.

To my mind the discussions should be based on personal experience and
knowledge.

The situation as shown in Shelly Batra's discussion can be seen as a
typical situation in under developed countries as well as in some
developing countries. The living conditions are ghastly, but because the
people have been living in those conditions for generations, it has
become an accepted standard to them because they normally have no other
option.

This is a cycle that needs to be broken, but it will not be easy.The GHD
community should also concentrate on finding affordable solutions to
assist health care workers countries who are in this position.

Because of the lack of maintenance and funds in resource limited
countries, the most economical method to be used will be the use of the
prevailing environmental conditions. This will normally be a challenge,
but the result will make it worthwhile.

Dries Meyer.

2:43 AM, 9 Nov 2011 | Permalink

33

Hennie Mostert

In my opinion the only way forward is to get Corporate Companies involved to sponsor the use of UVGI. The cost factor limits hospitals to realise the true potential of the technology and by installing 20 or 30 units accross a large hospital you are generating a false sense of security. In contrast if you could install 100 or 150 units it will dramatically change the outcome of the game. It is all about travel time and multiple periods of irradiation. But to have so many units in a hospital has its own problems. Upper air units will not work due to reflectivity off the walls so wall mounted units would be the way to go. They are safe and the irridiation is done in a closed environment (enclosure or box). The cost of such a roll-out is still the prohibiting factor and if corporate companies are asked to sponsor such units they will require some sort of possitive PR in return. Possibly this could be linked to the CSI of such corporates???

8:56 AM, 16 Feb 2012 | Permalink

34

Hennie Mostert

Still on the topic of costs, as far as I am concerned the cost of the technology is its own limiting factor. UVC and UVGI manufacturers have to design and manufacture their devices with the cost of production and a possible sales profit in mind. They only have one opportunity to sell the unit and make a sale profit, and at the end of the day it is still a business that needs to pay salaries etc. The cost of production may interfere with optimal functionality and effectiveness of the unit. Surely if you take a normal wall mounted unit with fans on each side to induce flow communication between the air and the lamps and you install 4 x 15W UVC lamps in it, surely that will render better results than a small unit with a 9w lamp. The travel time may be short in closed wall mounted units but if you add stronger lamps and have reflectivity inside the unit you can increase the starting UVC lamp power to almost double, although the reflectivity is achieved by means of alluminium which is costly. The wall mounted units are closed units so General Health & Safety standards will not be ...

expand comment

10:01 AM, 16 Feb 2012 | Permalink

35

Edward Nardell, MD

More responses to your UVGI questions.
On Feb 16, 2012, at 10:02 AM, GHDonline (Hennie Mostert) wrote:

Hennie Mostert replied to the discussion "Engineering control" in the TB Infection Control community.

Reply contents:
"Still on the topic of costs, as far as I am concerned the cost of the technology is its own limiting factor. UVC and UVGI manufacturers have to design and manufacture their devices with the cost of production and a possible sales profit in mind. They only have one opportunity to sell the unit and make a sale profit, and at the end of the day it is still a business that needs to pay salaries etc. The cost of production may interfere with optimal functionality and effectiveness of the unit.
EN: We are working to produce a standard international UV fixture design that would be inexpensive and reliable. We are not there yet, but working on it in collaboration with UP and researchers at Harvard.



Surely if you take a normal wall mounted unit with fans on each side to induce flow communication between the air and the lamps and you install 4 x 15W UVC lamps in it, surely that will render better results ...

expand comment

10:42 AM, 16 Feb 2012 | Permalink

36

Robert Spiteri

The main question here is that of cost versus longevity/design.
The cost of the unit falls away within the first year. After the first year on many units, the lamps need to be replaced as their efficiency will have dropped by +/- 40%. This is true of smaller wattage lamps.
With the lamps that are +/- 18 W and above it is possible to optimise performance to give longevity to the units with extended lamp life of 2 years or more. This has been proven by many of the users by monitoring the lamps on a regular basis thus making this particular unit of UVGI cost effective. Hospitals and clinics in South Africa that have used these particular units monitor their UVGI systems using the UVC meter every 6 months. In a survey carried out by myself, all have reported back no early lamp life failure. It is important to monitor UVGI systems and take meter readings at regular intervals. This plays an important role in cost effectiveness knowing when to replace the lamps other than being told to replace the lamps every 12 months by the manufacturer.

Sponsorship and branding by companies is only but a limited success as the ...

expand comment

2:35 PM, 16 Feb 2012 | Permalink